faults in a MV net

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #1664
    Tibese
    Participant

    in my company we have incoming 15kv from utility and the utility transformer step it down to 3kv. for emergency we have 2MVA generator. this days we are having a problem in that the when the utility is down the generator starts but fails to energize the breaker( or it makes breaks) anyone with such experience?

    #1677
    Ali Sepehri
    Keymaster

    Hi
    The problem is very general.
    You must check many characterizes in your MV network and analyze with details.
    I think you must check switchgear relay section or your breaker making current capabilities to make your generator to network.
    If you give me your email address i can send you a useful PDF about this issue to you.
    Thanks